Replies: 4 comments 7 replies
-
Fairly certain when charging from AC the maximum is 1KW. My SE7600H-USSNBBL14 will only grid charge the same at 1KW as you have observed. I can get up to 5KW from solar as well. I am not able to find a relevant spec sheet that shows this value, however hopefully the knowledge is helpful. -darkwind |
Beta Was this translation helpful? Give feedback.
-
Hmm, there appear to be a couple of people posting in the HA-forum where things appear to work up to 5KW - such as here or here. I can of course not rule out that they have a different inverter from mine. |
Beta Was this translation helpful? Give feedback.
-
OK, found my problem. I had not set |
Beta Was this translation helpful? Give feedback.
-
@AMichaelSuess Do you maybe have a setting or combination of settings to only use grid power to charge the battery? I mean disabling input from solar power and only charge the battery by grid. When I set |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
Dear all, also trying my luck here, as maybe somebody with a home battery can help. When I change the
Storage Command Mode
toCharge from Solar Power and Grid
, my battery charges with less than 1KW. It usually is able to charge with 5KW - and I have seen it doing that on solar power. I have theStorage Charge Limit
set to 5000W - and changing that also while the operation is running does nothing to increase the power. I haveAC Charge Policy
set toAlways Allowed
- therefore also noAC Charge Limit
is set - or should be set according to the documentation.So what am I missing? How do I get my battery to charge with full 5KW power? If anybody in this round has any ideas - I would appreciate any pointers! Thanks!
Beta Was this translation helpful? Give feedback.