Site limit control not working or lagging behind #645
Macgregorsound
started this conversation in
General
Replies: 1 comment 2 replies
-
I think to change the Site Limit (solaredgemodbus_i1_site_limit) you need to send a "Commit" and that effectively resets the inverter. It isn't a viable thing to change regularly because of this as it takes 1-2min to come back online (on my system at least). If you want to stop the system generating/exporting energy, then the way to do that is by using solaredgemodbus_i1_storage_discharge_limit as that doesn't require a restart of the inverter and takes effect quickly. |
Beta Was this translation helpful? Give feedback.
2 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
-
Describe the bug
When changing the site limit of the setup, the active power limit goes to 90% and the system does not listen to the site limit value. Sometimes after 2 hours it will respond and start working as expected.
Expected behavior
Site limit is set from 55000W to 200W max export, the system should then start to run in zero-export mode (solar keeping up with internal consumption)
Screenshots
No response
Diagnostic File
config_entry-solaredge_modbus_multi-683527698ba1cdcabcb907ad3651c797.json
Debug logs
No response
Home Assistant Version
2024.7.4
solaredge-modbus-multi Version
2.4.18
Installation Type
HAOS
Read the Instructions
Additional Context
No response