I have question about the SolarEdge active power limit and hope someone can help. In the MySolarEdge app you can read the inverter active power limit as a percentage. When reading the modbus Sunspec registers, all known (to me) registers for reading power limit percentages always stay on 100%. Name Address dec / hex They all always return 100%
|
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 15 replies
-
There isn't a calculation, the registers are a direct read. Example in code for Decoded as a 16 bit unsigned integer, and the value is returned directly to HA. So if that value never changes, something else is happening or the inverter itself has a firmware bug. |
Beta Was this translation helpful? Give feedback.
-
I eventually found the answer on my original question about the powerLimit % in the MySolarEdge app when throttling and in hindsight it's pretty obvious. |
Beta Was this translation helpful? Give feedback.
I eventually found the answer on my original question about the powerLimit % in the MySolarEdge app when throttling and in hindsight it's pretty obvious.
It's not in a separate register but a calculated value. When the inverter is throttling (register 40407 value 5) , it's the actual power (register 40083) divided by the maximum power limit of the inverter (register 62220).